I have a layout with two isolated sidings. Still in the process of finishing the layout with scenery and such. Have had the layout operational for over a year and never had any electrical problems.

Parked one engine on the siding to operate the other engine. Apparently did not have the parked engine all the way in and left the power on to that siding.

While operating engine two I saw that engine one still had power. I shut everything down. Apparently I had power going to both isolated sidings.

When I went to start the layout  again. My outlet on the wall  was dead. I checked all breakers and GFI plugs in the house and nothing was tripped.

Any suggestions as to why the outlet is dead?? I do have a breaker on my transformer. It is an old post war Train Master Type TW. I did plug that in to a different outlet and it appears to be ok. Have not hooked it up to the layout yet.

 

Original Post

Replies sorted oldest to newest

Lionelski posted:

Sometime, with age and use, outlets just go bad, John. I doubt it has anything to do with the transformer, etc. Is that the only dead item on that breaker?

Probably a simple outlet replacement is all that is needed

Thank you was hoping I did not do anything catastrophic. I have two plugs that are withing 4 feet of each other they are both bad. Those to plugs are the only nonfunctional issues in the house.

Electrician here...

Sounds like a bad connection in one of the receptacle boxes. If you are comfortable investigating then turn the circuit off and open up the receptacles to check for loose wires. Start at the last working outlet on the circuit until you find the cause. If you find that it was a loose wire then replace that outlet. The heat can cause hidden damage. A decent multi-meter will help too.

If not then call a local pro.

John Patrick posted:
Lionelski posted:

Sometime, with age and use, outlets just go bad, John. I doubt it has anything to do with the transformer, etc. Is that the only dead item on that breaker?

Probably a simple outlet replacement is all that is needed

Thank you was hoping I did not do anything catastrophic. I have two plugs that are withing 4 feet of each other they are both bad. Those to plugs are the only nonfunctional issues in the house.

If you are not educated on home electrical wiring, I would shut the breaker off that controls those outlets and call a good electrician. There are a number of things that could be wrong and some of them could be serious. It's odd that two outlets go at the same time without a breaker failure. Although if it is age related, it's possible they are aging out. All the more reason to have an electrician check if there will be more going soon. However, it could be wiring, and that would be more serious and potentially dangerous. 

One last thing to check, is it possible those outlets are on a wall switch that got turned off?

George