At some point in my journey in this hobby I found myself using 16-Gauge stranded solid copper Speaker wire for my power distribution. 

I am using MTH terminal blocks and the MTH  Z4000 Transformer. 

I forget if someone shared this with me or I read about it or made the discovery on my own. 

From my point of view PRO's:

Wire is cheap and easy to get

Copper good 

Wire is 1 pair, with each wire is marked for easy identification of hot vs. neutral 

Getting to the point, I was at my favorite train shop a week or so ago ( Train Depot in Mt. Airy MD) I was talking with the owner and he seemed shocked that I was using speaker wire. 

He said I should be using track wire, that he happened to sell. 

The POINT, Is there any reason I should not be using 16-Gauge speaker wire? Is there a problem here or was I being sold something I did not need? 

I have been using the speaker wire for over 2 years now and I have never had an issue. 

Original Post

Replies sorted oldest to newest

If speaker wire works without problems, don't worry about it.

You use 12 or 14 gauge wire to minimize voltage drop. Voltage drop cause trains to slow down as they get farther from the transformer. Voltage drop usually occurs with lots of lighted passenger cars or multiple engines. also on big layouts. If the trains don't slow down, you are good to go.

geysergazer posted:

I use speaker wire: 12 gauge for the buss and 18 gauge for drops to the track. It looks like copper but is actually copper coated aluminum as most speaker wire is. It works fine. BTW, I use standard wire nuts for most connections.

The copper clad aluminum wire (CCA) is a bit more than a gauge higher in number than the pure copper (CU). That is, 18 gauge CCA is like using 20 gauge CU. So if you want the current carrying specifications as to voltage drop that 18 ga CU provides, you should go to 16 ga when using CCA.

By the way, All Electronics has all copper speaker wire.

I think the train store guy was thinking that all speaker wire is copper clad aluminum (it's not) and his "track" wire is probably all copper. My guess...