This house does and it has GFI on the outlets but what worries me is I am relying on the GFI because of the proximity of the trees water reserve to the various power leads.
So will the GFI still work? I dont want to risk anyone getting electrocuted.
|
Replies sorted oldest to newest
quote:tell your son to replace his recepticals forthwith.
I picked this up on a quick google search.
How a Ground Fault Circuit Interrupter (GFCI) Works
Figure 1: The 0.005 amp difference between the current going out and re- turning is sensed and the GFCI trips.
A GFCI (Ground Fault Circuit Interrupter) is a system that shuts down a protected electric circuit or opens it when it senses an unexpected loss of power, presumably to ground. GFCI protection devices constantly monitor and compare the amount of power flowing from the input hot wire and the amount of power returning on the output neutral wire. Any time the returning power drops even slightly below the amount being supplied (0.005A or more), the protection device will trip and therby open the circuit.
GFCI devices, including receptacles and circuit breakers, work by passing both the hot wire and the neutral wire through a sensor - such as a differential transformer (shown in the schematic above) - and connecting the sensor to a solenoid or relay that opens a switch built into the power conductors inside the device. See the schematic above for details.
You may have noticed that the working parts of a GFCI system don't include the circuit ground wire or the ground slot on a receptacle. That's because GFCIs are designed to protect us against a ground fault. A ground fault is defined as an unintended loss of power to ground through some path of least resistance - possibly through a person! The regular grounding system, on the other hand, protects the equipment that is attached to (or plugged into) the circuit against a ground fault in it. GFCI devices are designed to protect people, not equipment.
When it is working properly, a GFCI - or GFI - device will open and protect the circuit it is attached to - the fault path, which could be you! - 1 when the difference between the current coming into and the current going out of that fault path reaches 0.005 amperes. That's 5 milliamps, an amount most of us can't even sense. And thus a current we are safe passing through us. Making sure it is working properly is the reason for testing it once a month.
Note: sometimes "GFCI" is abbreviated "GFI".
So a ground fault device, either receptacle or circuit breaker, will work with out a ground wire present, though you have compromised equipment safety by lack of the gounding conductor. The Christmas tree lights don't have a ground wire, but a ground fault will still protect you and cause miserable problems on that outside circuit that is damp and wet.
quote:Originally posted by Dale Manquen:quote:tell your son to replace his recepticals forthwith.
I'm sure that this meant "first add green-wire safety grounding, and then replace the receptacles." Adding just U-ground receptacles without safety ground wiring gives a misleading and dangerous sense of security. (It also screws up installation of any TMCC/Legacy base wallwarts since you would expect the U-ground pin to connect to earth ground!)
quote:So will the GFI still work? I dont want to risk anyone getting electrocuted.
quote:Originally posted by Dewey Trogdon:
I snaked a #12 ground wire to all the kitchen, dining, basement and bath receptacles[new] in my parents two-wire romex house[1949 blt.] during 1966. Had to do a little plaster and dry wall patching in a few places.
Subsequent to the 1965 Code changes the State and Local departments recommended running a single ground wire as an approved upfit in older houses.
quote:Originally posted by Blystovski:quote:So will the GFI still work? I dont want to risk anyone getting electrocuted.
I just wanted to back up Mike CT's post above - your GFCI will still protect against ground faults even without a grounded socket.
quote:Originally posted by Tom Tee:
Sparkies, why do GFCI's experience "early" failure? Over the years I have had several relatively young GFI's / GFCI's fail to hold a healthy circuit, had to replace. A lot like our model trains, untested until out of the box. There are better grades. Kitchen, laundry area GFI should be 20 amp rated.
What contributes to random GFCI short life cycles? They seem to be subject to surges. Lighting (other surges) seems to seek them out.
Additionally, what are the added qualities in a weather resistant GFCI? Would it be smart to use all "W" GFCI's in normal basements? Not a whole lot. Weather proof probably includes a gasketed cover. Common exterior practice is a bubble cover that allows for complete weather containment of a plugged in cord.
What is the very best (above the code) way to ground csst yellow sleeved gas line? Change the term to "Bond", which applies to both water and gas piping systems.As we move both systems to more modern non metallic containment, especially from the street in to the residence, there are still components of both systems that are metal. A Bond to an electrical ground system, hopefully at Zero volts, is an assurance the metalic parts won't become energized. Commercially, structural steel is also required to be bonded to the electrical ground system. Most bonding to either water piping or gas piping is done with usually a #6 solid bare copper wire, I have seen #4 solid Aluminum wire used for the same purpose. As interior plumbing becomes more and more non-metallic, I'm sure there are code provisions for the small brass fittings, lav, shower, tub fixtures and water tanks, still metallic but I will admit to not being too keen on that, Most buildings I've worked in, had complete metallic water and gas systems. I'll push that one off to your local code enforcement officer who has the ultimate word anyway.
Just want to get as much mechanicals done b/4 the layout gets too far along.
We are not talking about a ground, note the distinction of the word "bond"quote:Originally posted by Ken M:
The NEC (National Electrical code)does not allow ANY gas pipe to be used as an electrical ground. Water pipe, driven 10' x 5/8 rod & many times both but never never a gas pipe.
quote:Originally posted by TMM:
Instead of listening to opinions and advice from this forum I would suggest you consult a licensed electrical contractor and/or the AHJ (authority having jurisdiction, electrical inspector) in you area with any questions you may have regarding electrical installations.
While there is a electrical standard NEC (National Electrical Code) some areas may have requirements above that of the NEC. The NEC is a minimum requirement.
Any idiot can hook up a circuit and have it work. Remember the NEC is a fire code the circuit you hook up must be installed in a manner in which it will clear a fault safely, not just work.
This was not intended to offend anyone on this forum.
TMM
I started reading this thread but stopped when I realized that I didn't understand it. So let me outline my problem and see if you guys can tell me why my GFI is tripping:
The electricity for my trains is on a circuit by itself; the breaker at the 200amp panel for that circuit is a 15 amp Cutler-Hammer GFI. I've had no problems with the 4 outlets on that circuit. I've used those outlets for my KW transformer, a shop vac, various power tools and a cordless phone charger. Not all at once, of course, but my point is I've used a variety of appliances on that circuit with no problems, OK? Enter a Dell pc (Optiplex GX260 SFF) and the circuit blows immediately on power up. With nothing else powered up, just this old pc (which still works well on other circuits in the house) the GFI blows when the pc power button is pushed. Why would a computer trigger the GFI?
The guy at Home Depot says I have an "open ground." The computer and monitor have grounded plugs; the powered pc speakers have a 2 prong plug.
Why am I having trouble with the pc?
In the picture below the pc is plugged into a different circuit in the attic.
common sense would pretty much answer this......no..
Agreed Aurthur, However the one problem I ran into was that when my home was built in 1965 ground was not required in rooms other than the Kitchen, Laundry, Garage and outside.
In my various remodel projects I have been adding ground wire back to the panel where I can.
I started reading this thread but stopped when I realized that I didn't understand it. So let me outline my problem and see if you guys can tell me why my GFI is tripping:
The electricity for my trains is on a circuit by itself; the breaker at the 200amp panel for that circuit is a 15 amp Cutler-Hammer GFI. I've had no problems with the 4 outlets on that circuit. I've used those outlets for my KW transformer, a shop vac, various power tools and a cordless phone charger. Not all at once, of course, but my point is I've used a variety of appliances on that circuit with no problems, OK? Enter a Dell pc (Optiplex GX260 SFF) and the circuit blows immediately on power up. With nothing else powered up, just this old pc (which still works well on other circuits in the house) the GFI blows when the pc power button is pushed. Why would a computer trigger the GFI?
The guy at Home Depot says I have an "open ground." The computer and monitor
have grounded plugs; the powered pc speakers have a 2 prong plug. As was mentioned the GFCI should work even if there is an open ground. Indication from the GFCI is that there is a fault or leakage. Keep in mind a very small leak of .005 amps, 5 milliamps, will cause the GFCI to trip. The reason they can be a PITA especially in damp locations. If the computer has a metal cabinet and it is setting on a concrete floor it could be leaking through the chassis ground to the concrete, but most likely is leaking to the equipment ground conductor that is installed via the 3 prong plug and grounding system present. I would try the computer on another GFCI circuit, note the portable GFI pictured above. If the same results, it's a computer problem, most likely in the power supply. Keep in mind I'm often wrong, at least the first time. Mike CT
Why am I having trouble with the pc?
In the picture below the pc is plugged into a different circuit in the attic.
I reviewed this thread, most of it from a year ago, Christmas 2011. I did edit some of my input adding color to high-light questions and answers. A lot of very good information, IMO. Some very good technical safety discussion via this forum.
But what do I know.
Thank you all who contributed.
Mike CT
" I would try the computer on another GFCI circuit,"
I'll try that and post the results, but it my be a while. The only other GFI circuits in my house are in the kitchen (You can imagine what a wreck it is the day after Christmas!) and the bathrooms (not much room in there either).
"If the computer has a metal cabinet and it is setting on a concrete floor it could be leaking through the chassis ground to the concrete."
Attic floor is made of plywood and the Dell pc cabinet is plastic, so ....
"most likely is leaking to the equipment ground conductor that is installed via the 3 prong plug and grounding system present."
Huh? Say that again in English, please. I don't understand it.
" I would try the computer on another GFCI circuit,"
I'll try that and post the results, but it my be a while. The only other GFI circuits in my house are in the kitchen (You can imagine what a wreck it is the day after Christmas!) and the bathrooms (not much room in there either).
"If the computer has a metal cabinet and it is setting on a concrete floor it could be leaking through the chassis ground to the concrete."
Attic floor is made of plywood and the Dell pc cabinet is plastic, so ....
"most likely is leaking to the equipment ground conductor that is installed via the 3 prong plug and grounding system present."
Huh? Say that again in English, please. I don't understand it.
It's an internal computer power problem, most likely with the power supply, though it would not be uncommon for equipment grounds to be used this way. Again 5 milliamps is very small. Not to say the computer wasn't built that way.
Some RFI filters shunt their energy to ground, which can trigger GFI circuits if conditions are right. There can be RFI on the power supply, caused by line power conditions, and/or coupling of RF energy of the load. Computers can have a lot of RF energy on the load, especially if the decoupling circuits are not working effectively due to design flaws, component aging, etc. So the root cause could be a number of
things, or a combination of non-optimal circumstances.
-Mark
quote:Enter a Dell pc (Optiplex GX260 SFF) and the circuit blows immediately on power up. With nothing else powered up, just this old pc (which still works well on other circuits in the house) the GFI blows when the pc power button is pushed. Why would a computer trigger the GFI?
I had a somewhat similar experience with my vibratory polisher.
It would work fine on any non-GFI circuit, but after running a few minutes on a GFI circuit it would trip the GFI.
The issue turned out to be a faulty white wire running to the motor. It was making intermittent contact due to the wires breaking little by little from the vibration. I reterminated the wire, and the problem was solved.
I had a somewhat similar experience with my vibratory polisher.
It would work fine on any non-GFI circuit, but after running a few minutes on a GFI circuit it would trip the GFI.
The issue turned out to be a faulty white wire running to the motor. It was making intermittent contact due to the wires breaking little by little from the vibration. I reterminated the wire, and the problem was solved.
Exactly what a Ground Fault is suppose to do.
Arthur P has great advise...
I would offer also to be mindful of the existing wire in Guest's son's home...Replacing the existing two prong outlet with two prong u ground plugs will not meet code nor requirements for; the power strips circuit breaker function. Most early homes had metal outlet boxes and a single continuos wire connecting all of these boxes back to the sub panel. you need to add a ground jumper from the new outlet to the outlet box with a green ground clip to insure the CB trip functions.
juist my six bits...