Skip to main content

I can't find any recommendations, but assuming all 180W Powerhouses are on, how many would be allowed on the same house circuit 20W/110V. 

 

An even finer breakdown would be how many per plug, 2 per outlet, with say 5 outlets per 20A/110V house circuit?

 

If I used a 12 Outlet Power Strip 120V Input Voltage 2400W Maximum Power, on one 20A/110V circuit how many 180W Powerhouses could safely plugged in?  Would that be 13?

 

I don't have any references to help me.

Original Post

Replies sorted oldest to newest

Well, assuming about 85% transformer efficiency, (and I suspect they're better), each transformer would consume about 210 watts.  If you assume you can draw around 2000 watts safely from that outlet, that would be nine transformers.  It would be somewhat foolhardy to try to draw the absolute maximum, and you also have to consider the power factor issue since the transformers don't present a purely resistive load.  Another consideration is the circuit breaker may trip after it runs for some time at the full rated load.  Quite frankly, I'd probably limit a single circuit to around 8 of them.  Also, I'd want to split the load between the two phases in the panel so that all this reactive load wasn't on one side of the line.

Originally Posted by marker:

I can't find any recommendations, but assuming all 180W Powerhouses are on, how many would be allowed on the same house circuit 20W/110V. 

You would probably be fine with 12-15, as there is not really any practical way to load them all fully to near 2 amps each.
 
 
Originally Posted by gunrunnerjohn:

Also, I'd want to split the load between the two phases in the panel so that all this reactive load wasn't on one side of the line.

Don't do that for power on the same layout.  That's just asking for trouble.

Last edited by ADCX Rob

I disagree with the contention that you can't run them on opposite sides of the 220 input.  It's perfectly in phase, the issue would be that you'd have to properly phase them by reversing the plug for the one side.  That does involve having them plugged in backwards to what you'd have on the other 110 leg.  On the plus side, it's not good to have a lot of inductive loads all on one side of the incoming voltage.  The secondary is totally isolated from the primary, or at least it better be!  So, there would be no problem here, other than the previous mentioned phasing adjustment.

Originally Posted by Jeff Metz:

My understanding was the 180 watt was the rating on the output at 18 volts, 10 amps. No the amount of wattage used at 110 volt. I'm sure someone more qualified will be able to correct and or explain better. 

That is correct, but there will always be some loss between the primary & secondary.  Loaded to a full 180 watts output, there will be a realistic 200-210 watts, or just under 2 amps draw on the AC mains.

Originally Posted by Jeff Metz:

My understanding was the 180 watt was the rating on the output at 18 volts, 10 amps. No the amount of wattage used at 110 volt. I'm sure someone more qualified will be able to correct and or explain better. 

John already talk about it, it's call transformer efficiency, if a transformer is 100% efficient, the secondary will have the same wattage than the primary ,  so a 180 watts at the secondary ( 18 V x 10 A ) will have at the primary   120 volts X 1.5 A  = 180 watts,  but the transformer is  not 100 % efficient.

Post
×
×
×
×
Link copied to your clipboard.
×
×