Thanks for posting the clear schematic.
From the dept. of continuing education...
I re-read the section of Barry's book regarding passive mode, and have some questions.
1) The book says that the disadvantages of passive mode usually outweigh the benefits, and that the main reason is to prevent over 12 amps from passing through the TIU (p. 119-120 in 3rd edition). I looked at my Z4000 and the MTH brick for the Z1000; the largest breaker on any of them is 12 amps. So, I'm wondering - how could one put more than 12 amps through the TIU if using a power supply from MTH (or any supply with a 12 amp or less fast breaker)?
Because, the transformer can deliver higher than 12A, hence why they limited to a 12A breaker, Further, it's a thermal breaker, so for how long and how much higher will it pass higher than 12A BEFORE it trips? Besides that, even when circuits are rated for higher amperage- as you cross a 10A threshold there is so much power that it will find a weak link- a less than ideal solder joint, a less than ideal contact or mechanical connection. A KNOWN weakness and still present in the WTIU is the ring terminal wiring to the binding posts is STILL a physical connection. When not if, you pass high current through those and one heats up and softens the plastic- that reduces the tension, resistance increases, now gets hotter, it both oxidizes and gets looser- even more resistance- total failure.
2) There's no mention of chokes in the book, so I did some searching regarding function and available items. The function makes sense to me, but I'm wondering about the size. Seems like the choke should be capable of handling the expected maximum load, so it looks like a 3 to 8amp toroid coil would fit the bill. One example from Amazon has a description of "uxcell a13071500ux0187 10 Piece Toroid Core Inductor Choke Wire Wind Wound 22uH 21mOhm 3 Amp, Coil" (the 3amp was the only one with the part number in the description). Do you agree about needing to handle 3-8 amps? (All of the chokes were under $2 each)
The choke needs the current rating of your power source + some margin. So generally, I would find a 3A rated choke would not be the right size.
3) I never run more than 2 or 3 trains thru my TIU. I had considered switching to passive mode to protect the TIU, but after re-reading the book I'm not sure that it's of much benefit. Do you think passive mode is worthwhile when running no more than 3 trains?
This is somewhat of a personal decision and highly suggest you do a risk matrix analysis:
#1 What is the cost of even one failure- to replace or pay for repair of the WTIU? These are roughly $400 street price.
#2 what is the likelyhood of failure? Remember there are factors to this so it's not just one answer. How much current are we running? What about peak current situations? Can we be sure we never get the loose binding post failure- and that failure is further worsened by the current? Take into account the number of terminal per track- so 4 total in normal pass through mode- a total of 4x4 or 16 total failure points and any one failure is bad.
#3 What does passive mode cost? Some wiring and some right sized inductors. I have been using and recommending these https://www.digikey.com/en/pro...P1770TA-220M/5429725 however, that one is out of stock. This search is for 12A rated versions https://www.digikey.com/en/pro...pWqaRoQIAmstFzLy2yoA So back to the question- about maybe $5-6 per channel is what passive mode "costs".
#4 What is the disadvantage frequently brought up when using passive mode? That the TIU no longer kills output power with an emergency stop button request. My counter argument is- if you actually use emergency stop function- it required powering down the remote, powering down the logic of the TIU to reset. Now that the wireless is integrated, I don't know yet (just saw my order from TW for the new WTIU attempt on an old card) works the same way, but bottom line, it felt like emergency stop was a little too "emergency" and a lot less just stop and let me try again.
Thanks in advance.