Hello, Scrap Iron--
Here is something that you should look into, and which can still be done, even if you have finished your new layout in large measure. The thing is, if a short occurs on the circuit from which you "emanate" your green ground, you will get some kind of voltage rise on the house green ground wire for that circuit: 1) it can rise to above the 30-volt "hot" touch limit; 2) it can rise to 63 volts on a 125-volt day; 3) it can rise to more than that if the wiring was done in the days when the green wire did not have to be the same size as the hot wire; it can rise to 125v if the green wire does not continue back to the panel or if it has been connected to the hot wire.
I presume you would have detected the last condition, but if you worked with that breaker off, you might not have. For the other conditions, keeping the insulation on these ground wires is excellent advice from Gunrunner. What is happening is that with new houses, the interior is spray-painted with the boxes open and the wires hanging loose. So all the color-coded wires are some shade of white where you see them for hook-up. A problem? Yes, who'd'a guessed.
Now you mentioned that you have ground fault circuit interrupter devices (personnel protection?) (GFCI-5ma?), which have been required in unfinished cellars for some time. Remember that these come in higher amperages (-10ma for a freezer at times?), as well if those things are actually arc protection breakers with included GFCI (required with finished cellars AND a rare required retrofit--lots of controversy here), and that will be 20 to 40ma. Now 5ma will knock you off a ladder, and I am not allowed to say here what 30 ma will do. Initially some of these may have been downstream of panels, but that may be passe now.
I assume when you say you have GFCI's, you do and know you should test them monthly, and they are in the first outlet, feed-thru type. But others reading this may not know. And if you do not know the wiring history of the house, you too. So you have GFCI's on a circuit. This can have two meanings. First, you have 3-prong outlets supplied from a 3-wire circuit, and you are compliant with the GFCI in unfinished basement area, and all you have to worry about is if you decide to put a nice floor and some rugs in your layout room aisles.
Second meaning, it may be that someone has accommodated three-prong plugs by changing all the receptacles, while still having only a 2-wire circuit. This is permitted if the basement is unfinished and the circuits have GFCI added (this can also be done by getting a GFCI breaker taking only two spaces, twice or 4 times if you have the piggyback 15amp breakers). It is actually a more personnel protective solution than a grounded circuit from a regular breaker, because of the speed with which it operates. In any case, $2000 will usually fix you up with a new panel or sub-panel, which you usually need for arc breakers upstairs.
I cannot help you with arc breakers, except to say you only have 4 choices, and the range of the included GFCI is 20-40ma, depending on which manufacturer you choose. If you have a bare concrete floor, 20ma will be very bad or worse, and anything should be backed by standalone GFCI-5ma, IMHO. Here in Virginia we will be 3 years behind at least, adopting the 2017 NEC sometime after May 2020. This situation requires consulting an electrician to get the latest on the advances in technology, at the planning stage.
It is also possible to isolate the connection to house green ground by using a ceramic capacitor. There is a class of these rated for personnel protection, which will IIRC pass about 1/10th of the ground plane (cellar floor, etc) current generated by the TMCC wall wart. Of course, the 2017 NEC was worded to newly address the issue of making and repairing plug-in equipment, another controversy. Code changes are made between 3-year cycles at times.
--Frank